Micc readings on a 4 core 10 mm are 4 cores to earth 1.09 ohms and between cores 1.70 ohms tested at 500volts cable supplies main DB and off peak DB both backed up by 60 A bs88 fuse, what's the resistance reading likely to be before it goes bang?
 
If you mean megohms....

The highest voltage within the cable seems to be 230V (if main and off-peak supplies are on the same phase). Worst case leakage is then going to be from two line cores to two neutral cores and to the sheath.
1.7||1.7||2x1.1 = 0.6MΩ
230/0.6M = 0.4mA = total leakage from both lines
230²/0.6M = 88mW = power dissipation in leakage resistance

So it's not going to go bang like that. It would probably need to be between 10 and 100 times lower to get into a runaway situation, although at 6kΩ the cable sheath would probably get warm enough to drive off the moisture if it didn't track and flash over. What you can't tell, though, is whether that IR value is because of a tiny leak that has been like that for decades, or a recent damage that is going to get noticeably worse. You can sometimes localise the problem by warming the seals and any likely point of damage with a heat gun; when you get to the damp bit the reading will duck and dive as you heat.

OTOH, if you mean ohms....

It already went bang.
 
Tel, they say great minds think alike, I just happened to think alike first.
 
You're not getting misleading readings from a sub meter on the supply?! Try the heat test mentioned above just behind each seal, easier to see with an analogue insulation meter.
 
Sorry my bad ,yes Megohms, cable is 40 meters and around 80 years old, old imperial micc,
Thank you all for response
[automerge]1580844854[/automerge]
You're not getting misleading readings from a sub meter on the supply?! Try the heat test mentioned above just behind each seal, easier to see with an analogue insulation meter.
No nothing in between kmf and DB, meters before kmf, analogue do they still make them only joking
Thanks it was periodic, so cross that bridge if we get the repairs
 
Last edited:
As long as the fault is damp in one of the ends (and not pinholes in the sheath) and the sheath hasn't corroded badly, and you can access the ends for repair, it should be repairable. MI cable is amazing stuff.
 

Reply to When does micc short or go bang in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
572
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
I have an original 250w glow plug in my 8yr old pellet boiler that's used to light the pellets during the start up phase on my boiler. The boiler...
Replies
12
Views
2K
Hi guys, So, a friend of mine has a three phase 100a supply and wants to install 2 x three phase 20a fork lift chargers and a three phase car...
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock