G
GLENNSPARK
well you crack on then getting your Zs from (R1 R2)...i`ll just whip round with the loop tester shall i....Unless you have a method to do it "dead"?
i think i`ll take a measured value of Zs thanks...Both methods work ...... take your pick!
Continuity testing is at something like 11volts and if tested at the rear and found to be good then fair enough.
You are basically trying to fail a socket because it wont respond correctly (to you) to a voltage way below what it was designed for.
ELI testing will inject a simulated 26amps (at the designed voltage) down the line and give you your satisfactory reading, what more do you want?
As we can all concur outlets like sockets can give a false negative to a R1 + R2 reading
and a resistance that persists even after 230V applied is not a mirage.if you have a large difference then a socket change just to omit any bad contact issues but no need for any replacements if we are talking a small difference.
thing is...theres no set value for r1 r2 & rn...and thus (R1 R2) in the case of a ring..
can this be said for loop?
well...no doubt you walked off from this little post thinking `HA...thats told him then`....As I interpret it you can derive your value of Zs either by calculation ( R1 + R2 + Ze) or direct measurement then compare either to the BS7671 values.
I do R1+R2 measurement as my way of proving polarity and CPC on circuits. You could equally take an R2 reading for your CPC -- again both acceptable.
As a final check I take a measured Zs reading to confirm there is no high resistance through the C/B etc.. that my R1+R2 doesn't pick up.
Thats my preference, I like to work 'dead' as much as I can, so I derive by measurement and confirm by test!
But there are many ways to skin the cat ......![]()
well...no doubt you walked off from this little post thinking `HA...thats told him then`.....
I'm not sure I do concur, as I just said I trust Ohm's Law and my meter's R Low Ohms accuracy (got the calibration certificate to prove itand a resistance that persists even after 230V applied is not a mirage.
Well use Ohms law then and use your meters dc voltage as your value then use your operational voltage as the value and see the difference!
What kind of differences between front and rear measurement would you consider large and small in this context?
You forget we have blinkered views on products that we buy will be to a certain standard just because we expect it... as well as this copper is a medium reactive substance in the presence of moisture so internal contacts will oxidise in an atmosphere that is regular subject to damp conditions and also mucky contaminated plug pins can leave a residue in the sockets all of which can easily equate to a very small 0.5 ohms resistance.