why can't you use a 'live' test Zs value? Its a legitimate value in that it represents in-service conditions much more than a low voltage (R1+R2) test?
Because some of those in-service conditions might not be part of the design earthing arrangements, and therefore you would be in error to rely on them in a test. It's like how you have to pull the earthing conductor before measuring Ze. Take my case - I know there is an extra parallel path of 0.6ohms somewhere between my CPC and the MET. No idea what it is, how it is formed, what its nature is, whether I have any right to rely on it. Indeed the whole point of it not being part of my by-design CPC arrangement means I would be totally out of order to rely on it.
Let's say my existing CPC is too large to ever meet Ze+R1+R2 > Zsmax, and must and should fail. A Zs test takes advantage of that extra 0.6ohm in parallel that I have no right to take advantage of, and indicates a pass. Then the final circuit that the parallel path sits within is taken out of service. My circuit no longer meets 0.4s disconnection time, I have a dangerous situation, and my test failed to pick this up because it relied on a parallel path that I had no right to.
You may also loose your earth at a later date when the plumber is busy disconnecting/cutting all this green'n'yellow stuff getting in his way!
But then he's cut a by-design means of earthing / CPC that I had every right to rely upon. I can't mitigate against that. But I can mitigate against relying upon things that I shouldn't be relying upon.