Other than ideally you should do as little 'live' testing as possible (EAWR)
This old chestnut...again.
I'm sure the word is 'working'.
Live testing ain't 'Live working'. No one would ever be able to their job otherwise!
And if it passes on the rear but not on the front, do you call it a pass or a fail? Don't think I can get happy about calling it a pass if I know that actually in use it could fail to meet 0.4s disconnection on a L-E fault out front, within the plug.
This has been kicked to death in other threads as to where you take your test value ...... but for me, yes I use the result at the front of the socket. If after my inspection/investigation of said naughty socket I can't rectify the fault (e.g. loose terminal, dirty terminal etc ....) then I replace the socket and re-test!
I like to think when Im testing Im working ...... but each to their own interpretation of "working" :)
why can't you use a 'live' test Zs value? Its a legitimate value in that it represents in-service conditions much more than a low voltage (R1+R2) test?
Because some of those in-service conditions might not be part of the design earthing arrangements, and therefore you would be in error to rely on them in a test. It's like how you have to pull the earthing conductor before measuring Ze. Take my case - I know there is an extra parallel path of 0.6ohms somewhere between my CPC and the MET. No idea what it is, how it is formed, what its nature is, whether I have any right to rely on it. Indeed the whole point of it not being part of my by-design CPC arrangement means I would be totally out of order to rely on it.
Let's say my existing CPC is too large to ever meet Ze+R1+R2 > Zsmax, and must and should fail. A Zs test takes advantage of that extra 0.6ohm in parallel that I have no right to take advantage of, and indicates a pass. Then the final circuit that the parallel path sits within is taken out of service. My circuit no longer meets 0.4s disconnection time, I have a dangerous situation, and my test failed to pick this up because it relied on a parallel path that I had no right to.
You may also loose your earth at a later date when the plumber is busy disconnecting/cutting all this green'n'yellow stuff getting in his way!
But then he's cut a by-design means of earthing / CPC that I had every right to rely upon. I can't mitigate against that. But I can mitigate against relying upon things that I shouldn't be relying upon.
Too many ifs and buts Nick.
How much time and money are you prepared to spend on a Periodic, on what is essentially a safe installation at the moment in time you test it? Remember, what happens in the future is not your responsibility.
Then I think its best you keep to your way of testing and I keep to mine :)
different testers for different jesters
Continuity testing is at something like 11volts and if tested at the rear and found to be good then fair enough.
You are basically trying to fail a socket because it wont respond correctly (to you) to a voltage way below what it was designed for.
ELI testing will inject a simulated 26amps (at the designed voltage) down the line and give you your satisfactory reading, what more do you want?
Boydy
Testing and Working Live are totally separate things.
I've explained my stance on this in the past and I'm not typing it all out again.
You'll never change my mind on this subject! :-)
I'm not into changing peoples minds, Im just into exchanging views and having some health debate and banter!
I personally don't know your view on working/testing but I gather you see them as two seperate points whereas I don't. Hell the forum would be boring if everyone agreed on everything and we all became little clones ........