Discuss where is the regulation for must be 'suitable for location'? in the Electrical Appliances Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,604
Scenario...

2 x switched fused spurs located in a shower room. They are 610mm from side of shower, so outside zones. However, they could still get water on them from the shower so I don't feel they are suitable for the location. I can't find a reg for this though. is there one?

I realise sometimes its ok to install a switched FCU or a plate switch in a shower room (outside zones) but they still need to be suitable for location. I can see this written in the 'Electrician's guide to the Building Regulations', but it would be good to have a reg number.

Cheers 🙂
 
Scenario...

2 x switched fused spurs located in a shower room. They are 610mm from side of shower, so outside zones. However, they could still get water on them from the shower so I don't feel they are suitable for the location. I can't find a reg for this though. is there one?

I realise sometimes its ok to install a switched FCU or a plate switch in a shower room (outside zones) but they still need to be suitable for location. I can see this written in the 'Electrician's guide to the Building Regulations', but it would be good to have a reg number.

Cheers 🙂

You mean this?
1646564586991.png
 
The physical characteristics of such a switch is exactly the same as a shaver socket, concerning how close to the wall it will fit… which could be “not very well” if it’s a badly tiled surface.
That’s where any condensation on the tiles will run into.

So we’re back to the discussion of having regular switches in a bathroom.

Personally… I just don’t do it, whichever zone it might be in. I try to just have a flex outlet in the room, and the switch fuse outside.
 
512.2 External influences

512.2.1 Equipment shall be of a design appropriate to the situation in which it is to be used or its mode of installation shall take account of the conditions likely to be encountered.

From Part 2 Definitions, accessories are included in the definition of equipment.
 

Reply to where is the regulation for must be 'suitable for location'? in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
3K
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
548
Rewiring an old farm cottage… every wall brick and previous wiring not done well at all. I can’t locate any of the prescribed zones diagrams on...
Replies
12
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
611
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
421

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock