which is less dangerous DC 123V/20A or 50V/50A?
or does it not matter at all?

context is an 85 foot run on bedrock between solar panels and battery house. i've researched and gotten no definitive answer, just confused.
i'll probably end up putting this wire in rigid bonded conduit anyway but if one configuration is less deadly i want to do that.
i had read that DC below 60V was considered safe, but at 50A?
any help is appreciated.
 
I would say 50V/50A is 'safer'. Anything below 50V ac is generally considered to be 'safe' but it all depends on the circumstances. If there's no circuit protection at source, the 50A+ could be interesting if an animal chews the cable!

At 50V you will need a thick cable to avoid voltage drop. Using metric sizes I think a 10 mm2 conductor cable will give about a 6 volt drop, so you probably need bigger than that.
In the UK we typically use "steel wire armoured" (SWA) cable for on-ground/under-ground applications.
 
I would say 50V/50A is 'safer'. Anything below 50V ac is generally considered to be 'safe' but it all depends on the circumstances. If there's no circuit protection at source, the 50A+ could be interesting if an animal chews the cable!

At 50V you will need a thick cable to avoid voltage drop. Using metric sizes I think a 10 mm2 conductor cable will give about a 6 volt drop, so you probably need bigger than that.
In the UK we typically use "steel wire armoured" (SWA) cable for on-ground/under-ground applications.
thanks. planning on 4awg for the 50v/50a. a bit more wire expense this way but if its safer thats the way im going. it isnt a foot traffic area, but still...
ill look into that swa.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
usa maine
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
which is less dangerous DC 123V/20A or 50V/50A?
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
pablopablo,
Last reply from
pablopablo,
Replies
4
Views
412

Advert

Back
Top