Actually bq are owned by the screwfix group, not the other way round
Lol, you can spur 10000 sockets, so long as the cable is protected accordingly
Nothing wrong with a several sockets protected with a 5amp breaker, or a spured outlet, for the sake of argument a garage, outbuilding/ workshop. 3 twin-sockets, no problem. Problems occur because the cable and or the breaker exceeds demand.
Not good practice, but any halfwit could argue the supply cannot exceed the current carrying capacity of the cable because it is protected by the breaker.
This is normal cheap options and loads and loads of outbuildings are protected thus. There is nothing whatsoever wrong with it, in the real sense of
I get a few 'breakdowns' especially kitchen, ring main. Toaster on, washer on, kettle on, grill on. I've had also had oil filled elec heater on....my 32a breaker trips sometimes...Ahh, it would with 40amps or so eventually, sometimes instant, sometimes over a few minutes depending on whose breaker. Now try and tell the customer..err your load exceeds the breaker
But this is brand new (sometimes it is)...surely they have wired it up wrong then?
In effect they have, but it is by no means 'wrong' although they have skimped and cowboyed it. The circuit is protected correctly