from 4A2 no.40. ref. B applies when V < 20d, V being the height of the void, and d being the diameter of the cable. between floors, V > 20d. (unless its a very shallow void, in a house it's generally 300mm (ish))See Table 4A2 Number 40. Method C does not define a cable within a void.