So if they have TNS or TT then I can use the installation earth?
Also for the cable I'm probably gonna use 3 core 10mm SWA. But what if I used 2 core and used the armouring as the main earth? Crazy talk?

Without actually being on site an seeing the installation we can only guess at what you can or can't do.

I assume by 'main earth' you mean use it as the CPC? Yes generally it is acceptable to use the armour as the CPC, that is after all how the cable is designed to work. But you need to do the calculation to confirm its suitability, if you are unsure/want us to check your calculation then post the relevant information along with what your results were and we can have a look and help you.

If you do need to set up a seperate TT earthing system then you will need to consider how you are going to isolate the CPC of the SWA from the new TT earth you create.
 
One of the lads I work with is saying that the caravan will need a pitch. You know like a box with a caravan hookup point like a commando socket type thing.
I have looked in regs book and page 316 (721.510.3) says "where there is more than one electrically independent installation, each independent installation shall be supplied by a separate connecting device and shall be segregated in accordance with the relevant requirements of BS 7671"
Seeing as this person only has 1 caravan that leads me to believe that they won't need a pitch? I can run the armoured straight into the consumer unit in the caravan.
Have I misenterperated anything there?
 