Correct me if i am wrong but do we do calculations with 230 instead of 240 because of voltage drop, if your allowed 4% then 4% of 240 is 9.6v. 9.6 - 240 is 230.4 which is more or less 230V

I don't know whether I'm right or wrong, please comment

regards luke
 
Luke, basically no!

We have standardised at a Uo of 230V, instead of the previous 240V (I beleieve as part of CENELEC, harmonisation etc)

You work put the 4% of the Uo, so for 230 is 9.2V. I quite often use this in reverse in the v drop calcs, by putting 9.2 in as the answer and seeing how far i can go with a cable of set mV/A/M for a set design current

In the 17th, the V drop changes, aint got the details but there are different percentage values depending on your circuit.:eek:
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
South Yorkshire

Thread Information

Title
why calculate with 230 rather than 240?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
LukeScotty,
Last reply from
TonyM58,
Replies
1
Views
2,740

Advert

Back
Top