Discuss why calculate with 230 rather than 240? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
24
Correct me if i am wrong but do we do calculations with 230 instead of 240 because of voltage drop, if your allowed 4% then 4% of 240 is 9.6v. 9.6 - 240 is 230.4 which is more or less 230V

I don't know whether I'm right or wrong, please comment

regards luke
 
Luke, basically no!

We have standardised at a Uo of 230V, instead of the previous 240V (I beleieve as part of CENELEC, harmonisation etc)

You work put the 4% of the Uo, so for 230 is 9.2V. I quite often use this in reverse in the v drop calcs, by putting 9.2 in as the answer and seeing how far i can go with a cable of set mV/A/M for a set design current

In the 17th, the V drop changes, aint got the details but there are different percentage values depending on your circuit.:eek:
 

Reply to why calculate with 230 rather than 240? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Hi there I have a few questions related to the power ratings of certain devices and how this interplays with the fuse. The reason I am asking...
Replies
4
Views
950
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
758
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock