This shows what is called an “Open Ring”. Basically a ring main but fed via two protection devices. Switches shown in RED are ON. The ring is never a closed loop because the protection becomes unstable, as would a RFC in a house if fed by two 16A MCB’s.
You can see that the system is very flexible if there is a cable fault between two tee switch transformer units.
View attachment 9924
View attachment 9925

Thanks, i was hoping you would come up with a drawing...lol!!

You can actually have a closed ring if the two ends are fed from the same source, but the control and protection set-up, needs to be suitable for that configuration. Works on a similar principle to dual bus bar main Switchboards....
 
The reason we use ring mains was started due to a copper shortage in the 70s. Before that we wired everything in radial circuits

ONE of the reasons, it wasn't by any means the only reason!! This is an ongoing Myth that's done the rounds!! lol!!

And ring circuits have been around a dam sight longer than the 70's, but they were still singing the same tune about copper shortages ...lol!!!
 
Last edited by a moderator:
Well one day it will be plasma conduits instead of cable and gel pack relays for JBs, I saw it on Star Trek 20 years ago and they proficised most things correctly. We already have hand held communicators, ipads, memory sticks, and transparent aluminium (the one with the whales).

Oh yes, one bottle of rioja and I reveal how sad I really am! Who said "in vino veritas??"
 
Last edited by a moderator:
Dont forget the automatic doors! Although they dont sound as cool as they do on the enterprise
 