think what would happen if you had a fault downstream of a break. how could the fault current trip the OCPD when there is no path. the fault potential would sit on the exposed conductive part.
 
for the ring main

would i be right in saying that we can use lower csa cabling then if we used a radial. therefore if we had a break in the ring it would be like having 2 radials and the cable csa might be to small for the load which could cause fires, overloading, ect
 
Your on the right lines yes.

Maximum rating of 2.5mm is 27A

So you need the ring to be complete making it 5mm so that the 30/32amp protective device offers protection for your cable

If the ring was incomplete the protective device rated at 30/32amp would not offer sufficient protection, causing the cable to overheat and potentially cause a fire.
 

Reply to why verify the continuity of? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
757
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
237
I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...
Replies
3
Views
761
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
305
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
508

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock