Bill Gross
I have 35 to 40 year old 230v 3 phase motors that run sanding, grinding operations.
Can I run them on a 208 volt 3 phase system?
Can I run them on a 208 volt 3 phase system?
Hi Bill and welcome to the forum yes I have wired 3 phase motors rated at 240 vac on 208 vac, I’ve wired 4 ton HVAC units rated at 240vac on 3 phase 208 vac and never had no problems. Let us know what you come up with and good luckI have 35 to 40 year old 230v 3 phase motors that run sanding, grinding operations.
Can I run them on a 208 volt 3 phase system?
Hi,you will have to explain,if the 208 volts,is a product of generation,transformer supply,or a volt drop issue.
Carl I’m talking about 60hz but I’ve also worked on European machines which was 50hz208V is within the band of permissible voltage variants.
Now a question for you, is the equipment 50 or 60Hz?