Hi everyone.

to give you a picture of the installation my question relates to i will describe from the source to the furthest away point.

Starting off at a main isolator a 3 core & neutral wire armour cable runs for about 30mtrs and supplies a 3-phase distribution board. From this 3-phase distribution board there are 4 sub-mains cables that are ran to 4 separate appartments. (1 cable to each). Each appartment is small in size and for this question have two ring circuits for socket outlets.

Appartment 1 fed from L1 at 3-phase DB.
Appartment 2 fed from L2 at 3-phase DB.
Appartment 3 fed from L3 at 3-phase DB and Appartment 4 is fed from again from L1 at 3-phase DB. That 3-phase DB does also supply a few other low powered circuits but nothing else appart from Appartment 1 and 4 are supplied from L1. Hope thats clear enough. lol.

Anyway, my question. I carried out an Earth loop test on a socket in the furthest away appartment, appartment 4, supplied from L1. All the correct wiring indicator lamps on the Robin test Equipment indicated the wiring was correct, so i proceeded and test result was ok.

I carried out the same test on Appartment no 1, fed from the same phase and again the same result.

When i attempted to carry out the same test on the other 2 appartments ie 2 and 3, which are fed from phases L2 and L3 the RED Wiring Incorrect indicator light came on. P-E and P-N green indicator lamps were on indicating that was ok though.

Within the appartments all wiring is correct. The Robin test equipment is for single phase use only so it wouldn't detect a cross phase at source would it?????

Having not further investigated at this time im thinking the problem is from source to the 3-phase DB.

Any other suggestions guys.

Thanks.

Gary.
 
Perhaps the meter broke, i don't know what that meter you have is but you say you had a red light wiring incorrect indicator and two green lights indicating all was ok? Have you checked it with a voltage indicator?
 
Think I'd be buying proper test gear rather than rely on something with blinking lights on it first, but are you sure it's not cross polarity in the sub mains from the 3phase board to the dist. boards in the apartments?
 
Thanks for the reply.

I have tryed the test equipment back at the first appartment and was ok and tryed in my home.

The Unit is a Robin KMP4120DL Loop tester. I is not a multifunction tester, just three individual units.

240v was shown on the LCD on the tester.

Thanks.
 
Thanks for the reply.

I have tryed the test equipment back at the first appartment and was ok and tryed in my home.

The Unit is a Robin KMP4120DL Loop tester. I is not a multifunction tester, just three individual units.

240v was shown on the LCD on the tester.

Thanks.
What other tests have you done there? Nothing wrong with seperate meters as long as they're all working and callibrated
 
Start by checking for correct polarity leaving the 3-phase distribution board then correct polarity being recived at the apartments consumer units -- as suggested get a decent voltage indicator for checking this at the terminals!

If that checks out OK then I suggest you have an issue with how the circuits in the apartments have been wired (or the sockets you have tested).
 
Thanks again guys for the replies.


I know the wiring in each appartment are ok, ive carried out polarity checks there. Also each of the sub main cables have correct polarity. The test equipment has been calibrated.


I will need to check the polarity of the main armour supplying the 3 phase DB.


Correct me if im wrong, but i wouldnt expect the loop tester to pick up on a cross phase on the supply cable, it would only be able to detect L-N and L-E.


I will let you know what I find.

Thanks.

Gary
 
Hi snowhead.

These are new installs totally. nobody staying in them yet.

I will test L-E as you suggested. The Neutral problem is a good shout. It's not an issue within appartments.

Im not at job today but will be interested to get to the bottom of this on my next visit.

Cheers.
 
Do you get the same result on both RFC on appartments 2 & 3.

IMO the line and neutral are connected wrong and the meter is picking this up!

Any faults should of been found on dead figure of 8 testing !
 
Has this 3 phase DB the sub-mains, and these apartments been wired by yourself?? If not, why are you now involved, where is the sparks that's responsible for this installation??
 