Discuss Wiring of the future in the DIY Electrical Advice area at ElectriciansForums.net

DJCC27

DIY
Reaction score
1
Hi, have a new house. Seems much old wiring. Lighting and ring main all in 2.5 cable. Many junction boxes and so on. Recently an electrician put in a fused spur for the boiler which I had moved. He ran the supply to the spur up a floor to a junction box and from there back down to the fusebox which is 20 cm away through a wall. My question (one of them) is as I now have exclusively LED lighting what cable can be used for the lighting circuit? Would have guessed bell wire would do. Also, if one lighting circuit for each floor can the loft lights be incorporated into the first floor circuit? And do the lights in my workshop (40 metres away connected by external cable to a sub fuse box) need a lighting circuit separate from the ring main for the sockets?
 
Can’t use bell wire for lights. Minimum 1.0mm for fixed wiring within the property.

Loft lights can be linked into the first floor if you want. Unless it’s a loft conversion with habitable rooms, then I might use a separate circuit, but no requirement to.

The lighting in the shed can either be on its own circuit, or from a 3A fused outlet on the same circuit as the sockets. Can you determine how the shed is supplied? Is it already a spur from the house rfc, or on its own radial circuit from the board?
 
The connection from the house to the workshop is from a 40 amp fuse (I think) in the household fusebox to a sub fusebox in the workshop. There are lights and sockets in the workshop. I have not checked to see if there is a light circuit and a ring main.
Thanks for the info about 1mm minimum cable.
 
Can’t use bell wire for lights. Minimum 1.0mm for fixed wiring within the property.

Loft lights can be linked into the first floor if you want. Unless it’s a loft conversion with habitable rooms, then I might use a separate circuit, but no requirement to.

The lighting in the shed can either be on its own circuit, or from a 3A fused outlet on the same circuit as the sockets. Can you determine how the shed is supplied? Is it already a spur from the house rfc, or on its own radial circuit from the board?
The connection from the house to the workshop is from a 40 amp fuse (I think) in the household fusebox to a sub fusebox in the workshop. There are lights and sockets in the workshop. I have not checked to see if there is a light circuit and a ring main.
 
The other difference is that mains wiring needs an earth wire at every point in the circuit even if it’s not used with plastic switches etc.

We call it a cpc…. A circuit protective conductor. It protects the whole circuit.
 
The other difference is that mains wiring needs an earth wire at every point in the circuit even if it’s not used with plastic switches etc.

We call it a cpc…. A circuit protective conductor. It protects the whole circuit.
Thanks again. There is earth wire all over the place and almost every radiator has an earth attached. I will examine what I have in the workshop so that I know a bit better what I am asking.
 
Ah, now earth wires on radiators are not an earth wire, they are called a bonding conductor.


Yes. It’s very confusing.
 
  • Like
Reactions: DPG

Reply to Wiring of the future in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
839
I am adding a light fixture in a room I am restoring in my 160 yo house. I have ran a new 12-2 w/ground wire from the ceiling box to a junction...
Replies
2
Views
850
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
780
Hi, I am installing a new bathroom fan. We had an electrician who ran 14/3 into a junction box. The black feeds a led light and the red was...
Replies
1
Views
647
After 24 years my septic lift station pump and high water alarm needs to be replaced. It was tripping the breaker and the alarm was no longer...
Replies
5
Views
641

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock