jasewarn

Hi.
I have to connect up a Worcester Bosch Greenstar 12\18 OIL FIRED Combi boiler with the following;

2 CHANNEL PROG
Zone 1- HW( no cyl stat. no external 2 port valve)
Zone 2- CH Rads (room stat,2 port valve.)

UFH - 1 zone only so no UFH wiring centre
(prog stat,ufh pump,2 port valve,)

I plan to connect all controls externally in a wiring centre but the wiring diagram for the boiler confuses me. Do I connect a L N E direct to the boiler and wire all controls through LS LR NS (removing link between LS and LR) or do I need to run cables to the connections marked L N DHW CH on the other side of the boiler? The plumber intends to use the built-in diverter valve for the HW side.
Any advice you guys can give would be gratefully accepted.
Thanks.
 
hw on from programmer to dhw terminal and heating switched live to ch only problem you will have will be with underfloor heating pump if the rad circuit is calling for heat then underfloor pump will also come on need to use relay to separate the two
 
Ok but what if I connect the ufh pump live with the brown of the ufh valve and NOT the orange of the ufh valve? A demand from the rad circuit will only backfeed up to this connection and no further?? So, if I'm using the dedicated HW and CH connections in the boiler do I need to run a L and N to this area aswell? Also, you're saying I don't touch the LS and LR connections and leave that link in circuit?
 
doing it that way would mean that your pump would start pumping before the valve opens not really a good idea as would be pumping to a dead end boiler needs a permanant live and switched live supply
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Worcester Bosch Greenstar 12\18 OIL combi Boiler
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
jasewarn,
Last reply from
jasewarn,
Replies
5
Views
4,557

Advert