no...13A...as i told you...ooo i was using 32amps as my design current for voltage drop
the consumer unit at the front of the house on an inside wall so im not sure if theres a way to get the cable back to it.
no...13A...as i told you...ooo i was using 32amps as my design current for voltage drop
the consumer unit at the front of the house on an inside wall so im not sure if theres a way to get the cable back to it.
really it should be 6mm swa to the shed from the consumer unit and a seperate earth rod?
perry....stop conjecturing....do your VD calcs as i asked you to....i have given you all you need...not sure but i doubt h'ill use more than 2.5
only thing is Edd....once he`s got light in there....wont be long before he`s regretting not having an outlet in there n all.....He most likely just wants a light in his shed.. let install a 6 mm SWA from the CU stick a rod in, dig up the garden, wreck the house, just so the poor sod can see his potting plants...
Spur off ring, 4mm radial SWA. make sure RCD protected. let him pot the plants...
Now if its a work shop down there, well!!!!!!!!!! thats a diffrent storey
perry....whats your max percentages of VD for lighting and power?the volt drop is under the limit
perry....stop conjecturing....do your VD calcs as i asked you to....i have given you all you need...
you know your length of run....
you know what your Ib is
now check the mV/A/m in app f OSG...
work it out...no guessing please
the volt drop is under the limit