why a separate earth rod. take the main earth to shed. don't let's re-open this discussion again or i'll be out with archie.
 
Let him do it his way he the boss let us know what the earth loop inmepence is after after all,it's a learning curb for you
 
not sure but i doubt h'ill use more than 2.5
perry....stop conjecturing....do your VD calcs as i asked you to....i have given you all you need...
you know your length of run....
you know what your Ib is
now check the mV/A/m in app f OSG...
work it out...no guessing please
 
He most likely just wants a light in his shed.. let install a 6 mm SWA from the CU stick a rod in, dig up the garden, wreck the house, just so the poor sod can see his potting plants...
Spur off ring, 4mm radial SWA. make sure RCD protected. let him pot the plants...
Now if its a work shop down there, well!!!!!!!!!! thats a diffrent storey
 
He most likely just wants a light in his shed.. let install a 6 mm SWA from the CU stick a rod in, dig up the garden, wreck the house, just so the poor sod can see his potting plants...
Spur off ring, 4mm radial SWA. make sure RCD protected. let him pot the plants...
Now if its a work shop down there, well!!!!!!!!!! thats a diffrent storey
only thing is Edd....once he`s got light in there....wont be long before he`s regretting not having an outlet in there n all.....
give him some light..and he`l be up late at night.....
wirin up a dodgy socket outlet...lol...
 
not if he has lighting in there, it ain't. ( 18 x 13 x 45 )/1000 = 10.53V.
 