Hi folks first post
Trying to repair/refurbish a CH system for a friend which had stopped working. Worked on loads of Y plans faults in the past but never seen anything like this one

Glow worm Fuel Saver 50
Drayton Programmer
Honeywell Stats and 3 port valve.
Smashed room stat replaced

The system had stopped working. Initial testing showed boiler fan wasnt working. Bench test confirmed fan faulty and fan replaced.
With new fan installed still no output to spark generator and gas valve via PCB.

Pressure Switch restrictor checked, blocked, and cleaned.Operation confirmed.

Spark Ignition now working boiler ignites boiler cycling on and off. Boiler igniting even with programmer set to off (overrun?) and kettling which suggests to me pump isnt running in this state. Pump valve and tanks all situated in loft

More work and head scratching required. Any body experienced similar
regards
ilsonbhoysparky
 
Hi.

Sounds like a mid pos valve issue, as even with the programmer off it still has a permanent live present. But then if it is faulty and sending a call signal to the control box then it should be operating the pump also. Could the pump be faulty perhaps??
 
it sounds to me, if the pump is running the mid-port valve is at fault as you mentioned it kettling, thats a sign of overheat, and it could also be if the mid-port valve is working which as you know, feel the pipes and see, if its ok then the heat exchangers possibly blocked hence the kettling.
 
No not always mate, i have had many a time when the pump and the mid/pos valve is ok and its been the heat exchanger blocked, might not be in this case, but it has happened, unfortunatley its a bad do unless you are on somesort of maintenance plan with somebody, might as well get a new boiler.
 

Reply to Y plan problem in the Australia area at ElectriciansForums.net

Similar Threads

I had to wire in an extra 2 port valve today to protect a newly installed unvented cylinder (replacing the old gravity fed one) in a standard Y...
Replies
12
Views
1K
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
581
1 - Major supply fault, details unknown. By time I get there DNO already put in genny and are digging up road. 2 - Reason for call, heating not...
Replies
4
Views
581
Hello Guys, I was wondering if any of you nice chaps could lend me some advice. So I have an open vented heating system with a 3 port valve...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock