I thought SWA was ok cliped direct.., My plan was to do this then fixed to decking base once it reaches the back garden.

I've been searching the regs, looking at reg 522.8.10 and different Reference methods, where does it state SWA has to be buried and at 450mm?
 
Last edited by a moderator:
When i come in the house from outside i plan on using a couple of meters of 6mm t&e back to the Main CU.
This short bit of cable will be surface mounted in trunking, I know the armoured doesnt require RCD protection but does this short bit of 6mm T&E need it? as its kinda visable through its entire length.

Also when i test this will i have to treat it as 2 seperate installs?
1 for the supply cable from Main CU, Then a second for the CU in the outbilding?
Filling out 2 seperate EIC's? notifying both jobs seperatley to labc
 