A friend has a cooker, its currently plugged into the kitchen ring, along with wasking machine, kettle toaster, cappuchinco maker, etc etc.
The current cooker says "2650W" on side, its a single with a grill (mutually exclusive). Now I know the diversity calc (10A + 30% of remaining f.l. except if socket included etc) so no great shakes for this plug top oven as it probably only ever pulls 10A or less.
They've bought a new one, double oven, grill, 4800W stamped on side.
They won't let me open it and look at the book yet but my gut reaction was "separate radial, 4mm2 on it's own RCBO / MCB"
HOWEVER.
If you do the 10A + 30% thing (there will be no socket outlet) it comes out at about 3000W.
Now I do not plan to plug this oven in as I think it will potentially tip the kitchen ring over the edge anyway, but just wondered what you thought - would you actually put a plug on it and run it on the ring?
The problem i have is I do not know the precise detail of what each part of the oven will pull current wise, and therefore the maximum load. It might be for example that the two ovens want 1950 Watts each - far too much for a plug top.
What are your thoughts. I have told them it needs a separate circuit which they accept. But I cannot find a definitive statement in the BGB or the OSG but the sparkys guide to the building regs says
"It is recomm. that electric ovens are supplied by a separate circuit, however for lightly loaded circuits ovens of rating 13A or less may be connected into a ring final circuit"
- when I did the calc it came out at 13.26 Amps.
Kind of on the cusp!
The current cooker says "2650W" on side, its a single with a grill (mutually exclusive). Now I know the diversity calc (10A + 30% of remaining f.l. except if socket included etc) so no great shakes for this plug top oven as it probably only ever pulls 10A or less.
They've bought a new one, double oven, grill, 4800W stamped on side.
They won't let me open it and look at the book yet but my gut reaction was "separate radial, 4mm2 on it's own RCBO / MCB"
HOWEVER.
If you do the 10A + 30% thing (there will be no socket outlet) it comes out at about 3000W.
Now I do not plan to plug this oven in as I think it will potentially tip the kitchen ring over the edge anyway, but just wondered what you thought - would you actually put a plug on it and run it on the ring?
The problem i have is I do not know the precise detail of what each part of the oven will pull current wise, and therefore the maximum load. It might be for example that the two ovens want 1950 Watts each - far too much for a plug top.
What are your thoughts. I have told them it needs a separate circuit which they accept. But I cannot find a definitive statement in the BGB or the OSG but the sparkys guide to the building regs says
"It is recomm. that electric ovens are supplied by a separate circuit, however for lightly loaded circuits ovens of rating 13A or less may be connected into a ring final circuit"
- when I did the calc it came out at 13.26 Amps.
Kind of on the cusp!