these figues that the Supply authority will say depending on the supply.
Be carefull with TT systems as the supply authority will state 21 Ohms this is the resistance of there earth rod at the transformer. When you install an earth rod the combined resistancce of your rod + theres must be under 200 ohms.
From what I understand, their argument is that EAWR doesn't allow live working.
As such the Ze and Zs tests are not allowed, as Ze can be obtained through enquiry and Zs by calculation.
The EAWR does not allow live working yes i agree However it does allow for live testing as the live parts are exposed but there is no interference with the system exept the insertion of GS38 probes connected to a meter all of which comply to current safety standards.
Be carefull if relying on inquiery as i have found wrong presentation of cable heads with no earth at all.
If you are unwilling to pull fuses then note on a PIR as a limitation and take a ZS at the nearest point of origion where access can be obtained. (normally the main isolator.)
Yes, Rb = max 21 Ohms
Ra+Rb should be under 200 Ohms.
Or under 100 Ohms if you read BS 7430
Someone just removed the post I'm replying to, it looks like I've lost the plot!
As IQ has already posted, the EAWR do not distinguish between working and testing.
Sorry thought we'd strayed onto wether to test live or calculate Zs,model forms in Appendix 6 just asks for Zs doesn't state has to be measured or calculated.
EFLI testing is live testing. This Live testing involves working on or hear live conductors. It is unlawful to work on or near live conductors under Regulation 14 of the EAWR 1989 unless " it is unreasonable in all the circumstances for it to be dead".
Pinched the above section from an IET forum on this sam subject.
THe key words are "is it un reasonable in all circumstances for it to be dead" how do you do a dead ELI or RCD test? It has to be live so then work out a risk assesment. GS38 probes ect which means you then comply with EAWR