OP
Deleted member 26818
BS7671 allows for Ze and PFC to be obtained by enquiry, as such it is not whether it is reasonable for it to be dead, but whether it is neccessary at all.
RCDs and Zs at socket-outlets can be tested with out the need to expose live conductors, as would functional testing of switches and RCDs.
Zs for other circuits can be obtained by calculation.
As such, it would appear that the only test required to be conducted live with exposed conductors, is polarity of supply.
RCDs and Zs at socket-outlets can be tested with out the need to expose live conductors, as would functional testing of switches and RCDs.
Zs for other circuits can be obtained by calculation.
As such, it would appear that the only test required to be conducted live with exposed conductors, is polarity of supply.