Discuss Zs out of spec on an RCD protected circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

What I mean by that is the reading for an IR should be out of range and not a few Mohm. In terms of your question I would ask this.

If you did do an EICR that had this situation and it didnt have an RCD, you would talk to the customer and explain to them the situation. Would you disregard putting in a RCD as a cost effective solution to a problem or would you insist on a circuit rewire and rcd?
 
If I did an EICR as you and found this situation, then as it stands its a C2. Installing an RCD could arguably be masking a problem that should have every attempt made to remedy it. What if the high Zs value were caused by a deterioration somewhere that would get worse? If it was a 16th ed installation there is no requirement to install an RCD retrospectively as a work around for a problem in a particular circuit. Yes, I would always advise that an RCD is a very sensible measure, but it is not a cure-all and in my opinion should not be used to cover up actual problems
 
What I mean by that is the reading for an IR should be out of range and not a few Mohm. In terms of your question I would ask this.

If you did do an EICR that had this situation and it didnt have an RCD, you would talk to the customer and explain to them the situation. Would you disregard putting in a RCD as a cost effective solution to a problem or would you insist on a circuit rewire and rcd?
is this not like failing an MOT for a seatbelt not working properly but just installing an airbag instead of fixing the seatbelt??
 
Guys guys please read the regs and especially 411.4.9 and then 411.5.3 and in neither of these regulations is the word additional used

Additional protection is used for sockets and outside equipment in reg 411.3.3

Guys I know where your coming from and all your scenarios are for the blatant variation of an expected value. IE on a domestic lighting circuit that would normally be 0.70-perhaps 1.20 ohm and you get a reading of say 6+ ohm. Then yes you should flag it up but a code 3 is improvement recommended and not further investigation so be careful what you put

As I said there are other reasons you use an RCD in relation to Zs values. An example again in a light domestic unit a company wins a contract and they need to install some temporary welding machines. The existing protection device is a B type breaker but a D type is required for the influx. You measure the Zs and it fails on a D type. So when the owner asks you what do I do as I will only be using the units for a month.

We all say well

A) You need to upgrade the circuit to a bigger cable to reduce the value. Costly and he is not going to like that

B) You need to reduce the MCB size or Type, not going to work

C) You fit an RCD to bring it into parameters.

For anyone that has done the 2391 course will know that you are often asked how to bring an Zs into line and those are the 3 options.

The trouble with all things electrical there is so many ways to skin a cat. There are times when you will have a higher Zs for he protection device installed originally and you have options to counter this, which I have outlined. The same goes with testing you have to assess and judge on the case in front of you, and not blanket, it is is o it has to be that
 
Guys guys please read the regs and especially 411.4.9 and then 411.5.3 and in neither of these regulations is the word additional used

Additional protection is used for sockets and outside equipment in reg 411.3.3

Guys I know where your coming from and all your scenarios are for the blatant variation of an expected value. IE on a domestic lighting circuit that would normally be 0.70-perhaps 1.20 ohm and you get a reading of say 6+ ohm. Then yes you should flag it up but a code 3 is improvement recommended and not further investigation so be careful what you put

As I said there are other reasons you use an RCD in relation to Zs values. An example again in a light domestic unit a company wins a contract and they need to install some temporary welding machines. The existing protection device is a B type breaker but a D type is required for the influx. You measure the Zs and it fails on a D type. So when the owner asks you what do I do as I will only be using the units for a month.

We all say well

A) You need to upgrade the circuit to a bigger cable to reduce the value. Costly and he is not going to like that

B) You need to reduce the MCB size or Type, not going to work

C) You fit an RCD to bring it into parameters.

For anyone that has done the 2391 course will know that you are often asked how to bring an Zs into line and those are the 3 options.

The trouble with all things electrical there is so many ways to skin a cat. There are times when you will have a higher Zs for he protection device installed originally and you have options to counter this, which I have outlined. The same goes with testing you have to assess and judge on the case in front of you, and not blanket, it is is o it has to be that

What about 415.1.1 and 415.1.2 then??
 
What about 415.1.1 and 415.1.2 then??

415.1.2 specifies that if an RCD is used then the protective measures of ADS, SELV, Double insulation, or electrical separation must be used.
For ADS compliance, if the RCD meets the disconnection time AND all the other requirements for ADS are in place (including short circuit and overcurrent protection) then the RCD can be used as the means of disconnecting the circuit in the case of an earth fault.

Regarding the Zs out of spec for an MCB but in spec for an RCD situation you would need to consider if there was a fault on the circuit causing the high Zs, or if the circuit was designed that way.

If the test results do not come close to meeting the values you would expect from a theoretical assessment of the circuit then you may well consider that there is a loose connection or some such that could therefore be dangerous in the case of a fault and so code as a C2.

If the test results match with what you would expect from the circuit and so you believe there are no faults in the circuit, then the circuit is safe for use and will not present a risk and would therefore not be coded.
 
415.1.2 specifies that if an RCD is used then the protective measures of ADS, SELV, Double insulation, or electrical separation must be used.
For ADS compliance, if the RCD meets the disconnection time AND all the other requirements for ADS are in place (including short circuit and overcurrent protection) then the RCD can be used as the means of disconnecting the circuit in the case of an earth fault.

Regarding the Zs out of spec for an MCB but in spec for an RCD situation you would need to consider if there was a fault on the circuit causing the high Zs, or if the circuit was designed that way.

If the test results do not come close to meeting the values you would expect from a theoretical assessment of the circuit then you may well consider that there is a loose connection or some such that could therefore be dangerous in the case of a fault and so code as a C2.

If the test results match with what you would expect from the circuit and so you believe there are no faults in the circuit, then the circuit is safe for use and will not present a risk and would therefore not be coded.

Brilliant Richard I think I am pretty clear on this now
 

Reply to Zs out of spec on an RCD protected circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Question is does this DB really need RCD protection as there are only internal lights and sockets supplying this large building that used to be a...
Replies
13
Views
602
I'm interested how you would all approach this one. A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager...
Replies
20
Views
757
Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
448
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
618
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
706

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top