Discuss zs problems in the UK Electrical Forum area at ElectriciansForums.net
B
bethelec
Any clues??? Trying to test zs at Lv panel incomer fed from transformer. With main switch turned on and feed to site temps (offices, 110v trannies etc) on I get a voltage between neutral and earth. With main switch off so feed goes from transformer to lv panel incomer only I get open reading. I have disconnected earth link on earth bar and taken out earth that feeds earth nest but still no reading. All cpc's are connected. Any advice or pointers would be grateful as I am stumped
You should not have any voltage between Neutral and Earth, they should be at the same potential.
If you have voltage between Neutral and Earth when the installation is on then this is indicative of a poor connection, usually of the neutral conductor, to the installation.
Much more information needed.
If this is the incoming from a DNO transformer you should not be removing the N→E link! I would only contemplate it if the transformer is isolated.
Reply to zs problems in the UK Electrical Forum area at ElectriciansForums.net
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Today I came across an earth cable from the earth bar in the DB that went directly into the incoming neutral side of the main switch. The DB is...
Been asked to do some rewiring, and have said needs upgrade of consumer unit really Main question is regarding earthing - Zs reads at 0.45 ohms...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...