Even if it is PME you may well find there are earth rods already fitted, a lot of newer PME industrial units have earth rods fitted, a look around the perimeter of the building often you will see the inspection pits
I seem to think this is going to be more problematic than planned for.
Where's the problem?
-Install the charging point.
-Install this little length of SWA, connect it to the charging point.
-Install earth rods, utilise the root of this charging point and the rebar of the concrete pad as part of this, test it and add more rods as required then connect it to the MET.
-Test and fill in the paperwork.
-Send your invoice and get your money.
Not to the MET. The rod would earth the VCP only.
Why not? It'll be much better for the installation as a whole to have a decent earth nest connected to the MET than it will to have what is effectively a big external socket connected to its own earthing reference in such close proximity to the metal building bonded to the PME earth.
I'm so I'll just run 16mm swa to the charge point, connect it to the met, and also connect an earth rod in for good measure.
Ok so we have a plan of action, it says in point two, a rod of very low resistance. Can anyone telld what if says in 722 of the regs as have not got a BYB yet.
New posts
Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...