Even if it is PME you may well find there are earth rods already fitted, a lot of newer PME industrial units have earth rods fitted, a look around the perimeter of the building often you will see the inspection pits
 
I seem to think this is going to be more problematic than planned for.

Where's the problem?

-Install the charging point.
-Install this little length of SWA, connect it to the charging point.
-Install earth rods, utilise the root of this charging point and the rebar of the concrete pad as part of this, test it and add more rods as required then connect it to the MET.
-Test and fill in the paperwork.
-Send your invoice and get your money.
 
Not to the MET. The rod would earth the VCP only.

Why not? It'll be much better for the installation as a whole to have a decent earth nest connected to the MET than it will to have what is effectively a big external socket connected to its own earthing reference in such close proximity to the metal building bonded to the PME earth.
 
I'm so I'll just run 16mm swa to the charge point, connect it to the met, and also connect an earth rod in for good measure.

Ok so we have a plan of action, it says in point two, a rod of very low resistance. Can anyone telld what if says in 722 of the regs as have not got a BYB yet.
 
New posts

Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
309
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
387
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
588
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock