Discuss Cable size in the UK Electrical Forum area at ElectriciansForums.net
Why not? It'll be much better for the installation as a whole to have a decent earth nest connected to the MET than it will to have what is effectively a big external socket connected to its own earthing reference in such close proximity to the metal building bonded to the PME earth.
I cannot answer that TBH. Just does not sound right.
Why doesn't it sound right? Adding an extra earth electrode to the PME supply is only going to improve it and make your installation safer in the event of an external neutral fault. This is exactly what is recommended in the regulations for swimming pools fed via a PME supply and is required practice for PME supplies in other parts of the world.
I'm so I'll just run 16mm swa to the charge point, connect it to the met, and also connect an earth rod in for good measure.
Ok so we have a plan of action, it says in point two, a rod of very low resistance. Can anyone telld what if says in 722 of the regs as have not got a BYB yet.
I always start with 2off 8'x5/8" rods spaced 10' apart and then test that and work up from there.
The earth electrode(s) should be connected back to the MET, not to the end of your new circuit.
It just does not. I am not dismissing you or belittle your post. I am all ears and would like to understand more. I would have though somewhere in BS7671 it would say something like to earthing systems cannot be in one location. Guess guess guess. Not fact!!!!
don't get many swimming pools on the railways although the unions are thinking about this 'right' in there current talks.
Wont the fault then take the path with least resistance which is bound to be the PME earth which pretty much makes the earth rod pointless?
If the Rods can achieve around sub ohm Ra they will be effective, also the way I read it they are as backup in case of a broken DNO Neutral to keep Ut low.