Discuss New Consumer Unit in the Electricians' Talk area at ElectriciansForums.net
According to B7671 with each flat being a separate installation it would be Ze, however as already said with this being a hybrid system then technically it would be a Zs.
About as clear as mud lol, if I was filling in an EIC sheet for say a CU change I would put it down as Ze for your flat.
The DNO class it as TNC-S/PME for bonding purposes as this is still the most onerous situation in the event of a broken suppliers N to the TNC-S/PME head at the origin, so I can see why they class it as such.
How is a PME TP&N supply into a block of flats with several sub distribution supplies that are individually metered at each flat a ''Hybrid'' system?? Each of those sub-main CU'S/DB's will still be derived from a PME supply, so PME conditions apply throughout the building. Each flats supply will have a Zdb/Zs value not a Ze value. the Ze can only be measured at the MET at the incoming TP&N supply position.
Main bonding of service pipes etc within each flat, will still need to be taken to the flats EMT.
Your average 1930's built house is going to have suspended floors downstairs and T&G floorboards both up and downstairs, so spring a few floorboards and run a 10mm bond to where you need it.
Never seen a 1930's built house with T&G floorboards, T&G floorboards came in much later like 25 years or so later. In the 30's they would have been pretty thick standard butt floorboards, built to last rather than the much thinner early T&G floorboards, that are even thinner these day's. That's if you get to have floorboards it's now all sheet boarding...
And it is sheeeet, too!
Originally Posted by Engineer54 How is a PME TP&N supply into a block of flats with several sub distribution supplies that are individually metered at each flat a ''Hybrid'' system?? Each of those sub-main CU'S/DB's will still be derived from a PME supply, so PME conditions apply throughout the building. Each flats supply will have a Zdb/Zs value not a Ze value. the Ze can only be measured at the MET at the incoming TP&N supply position.
I was going off of UKPN documentation,
Yes it is TNC-S at the head or origin, of which there is only one.
Now according to BS7671 each flat is an installation in it's own right, as you rightly say they are bonded locally inside each flat as you would do if it was a separate install like any other.
If you are classing each flat as a separate install as above then technically that flat is a TNS, there is no CNE link at that head, the earthing to that flat is separate, yes it is derived from a TNC-S supply, now either that flat is classed as a separate installation or it isn't.
This is where the complication is, that flat has technically a SNE (separate Neutral Earth) however the bonding requirements are to be taken as TNC-S, it is where the boundary is actually drawn, either at the flats own service head as per BS7671 with it's own bonding requirement as you yourself pointed out above, or the whole block of flats classed as one installation.
It is all semantics really as the definitions of where each part overlaps, I called it a hybrid in "" as it is not always clear where the demarcation point begins and ends as far as we are concerned, our remit is only to BS7671, it does not extend beyond the suppliers cut out which may (or may not) be present in that flat.
I already said if I was replacing a CU in that flat that even though it would be technically (and correctly) a Zs but would record it as that flats Ze on the EIC, because that is where that particular dwelling/installation according to BS7671 ends (or rather begins :) ), the chances are we would have no access to the supplier switch gear anyway, in other words treat that flat as a separate entity, which is about all we can do.
The UKPN documents go a lot further than a simple block of flats, one example given is a modern industrial estate, now previously each separate unit had it's own CNE link in each (separate) building all bonded to the various services shared between seperate buildings, and was designated as a TNC-S/PME to that building, which is fair enough so far.
The DNO (UKPN in this case) has/had decided in an effort to reduce circulating N -E currents to put just one CNE link at the supply end (sub-station/switchroom or whatever) and supply each unit with an SNE (TNS) supply, however again for the usual reason where PME is concerned (broken suppliers N etc.) that the bonding requirements for these units will be as per TNC-S.
This is similar to above but on a bigger scale
Ps. I already said in the post of mine you quoted, or in one the others related to that subject that the DNO classed the flats supply as TNC-S/PME as far as bonding was concerned and rightfully so in my opinion, so I am not sure where or if you are disagreeing with me or not lol.
From experience I'd say T&G boards have been around a lot longer than that. But maybe it varies depending on where in the country you are.
eng. i have to disagree with you on this one. my parents house was T.G. floorboards, original from 1926. block parquet in hall and 1 living room.
or bloody laminate.
you cant get under the floor without replacing it or the ceiling below
I have to disagree on this one too ... there is no sign of the wholesale lifting and removal of the floorboards in my house, 1876 vintage T&G and well over an inch thick! The really sad thing is having to cut into good timber to deal with the Dry Rot! Most of it has ~ 32 growth rings per inch and is sounder than anything that you can get in the builders' merchants today.
I look like i still live in a cave tbh Tel, im sick of climbing out of a floor/loft space and hearing...
"Christ mate how long have you been in there?"
Well all i can say is that you are a ''One Off'' then!! But i suspect that the flooring has been professionally refurbished by artisans sometime in it's past. I wonder how in 1876 they found it cost effective to T&G 1 inch plus floorboards?? Did they have the machinery to produce T&G, i don't know??
... aren't we all ... 'One Off' unique in every way! To be celebrated for that which we bring to life.
On the construction front, I have no other point of reference as I have yet to get outside of my own house to others of similar ilk ... with the original floorboards still in! We dismantled the roof of a similar vintage property up the road, but the original floorboards were long since replaced as it was converted into a pub. We recovered: half a roof of diminished course Ballachulish slate, Scottish quarries in Glencoe closed in ~ 1950; 187? sarking boards and roof timbers, slight woodworm damage though almost half of rafters butchered by aforesaid conversion. We also managed to recover the dressed stone from the 3 Dormer Windows. When the demolition crew moved in almost 6 months later we recovered ~ 90 % of the sandstone.
Well it's not TN-S is it, so can't be classed as such!!
Being a separate installation does not mean the supply suddenly chances from PME to TN-S
It's no different than any large PME installation that comprises of multiple sub-main distribution circuits none of those sub-mains can or will be classed as a TN-S installation.
There is no demarcation as far as the type of supply provided by the DNO. If it's a PME supply then it will remain a PME installation throughout the installation derived from that supply. The neutral of that DNO supply still being the source of the only electrical earth throughout the whole installation....
It's only a separate entity in the fact that each flat is separately metered installation.
How can you call or record a Zs/Zdb value as Ze when it's clearly NOT? If you can't gain access to the main DNO supply then you record that on any certificate you need to produce
That's because they would be separate buildings, and each joint to the network distribution cable supplying each building would or should have the neutral conductor earthed, as stipulated in the PME requirements...
Then that is NOT a PME system is it, it's a straight TN-S system. Every TN-S system has a single point N-E connection at the TX or main switch board.... If the neutral is not being used as a combined neutral earthing conductor on the system, then PME/TNC-S bonding requirements is not required....
My comments in bold...
What i'm basically saying is, that T&G floorboards were not a common entity to be found in the 1930's or beyond. Maybe on the up market properties of the era, but not on normal builds, it wouldn't have made any economical sense whatsoever. I've personally never seen original 1'' T&G flooring on a 30's or beyond house, it seems some of you have..... Block/parquet flooring is a totally different kettle of fish....
Stop back peddling!! lol
Not back pedaling at all, i personally haven't ever seen T&G flooring on such old properties, it's always been well laid decent thickness butt floorboards. It seems some here have, now whether or not they have been refurbished at sometime in the past is another matter...
I've worked in plenty of old properties in up market area's like West London and the Suburbs and rarely will you find T&G Floorboards.
Maybe other area's around the country are different.
and my dad's 1926 built semi had cavity walls. now that's unusual too for the year. unfortunately the wall ties were not galv or s/s so rusted.
I have a red brick detached property in the UK built in 1931 (one of two side by side properties built by the same builder and still have all the builders plans and photo's, and even some of the original material invoices) that has cavity walls apart from the attached garage and integral storage room). The floorboards are as i've described in previous posts here. The joists are also a far cry from what you would see in today's cardboard built houses, most being 4'' or more wide. No need to worry about a few 25mm holes being drilled wherever you like for cables etc...
I meant to add as we need to test Ze and PSSC then it makes sense to do these tests together
Presuming you mean PEFC then really the earthing conductor should be reconnected before testing this, as with Ze you want the measurement through the earthing conductor alone but for PEFC you want any parallel paths which are likely to increase the prospective earth fault current for the installation.
Ok poor choice of wording on my account, SNE would be a better description, see my original paragraph justbelow :), and I am agreeing with you here in that is why the DNO are treating the whole installation as PME.
It is only different in so far as that as a dwelling it has a different definition as far as BS7671 is concerned, ie. as a separate installation, in other large installations such as a factory and the like these are not classed as seperate entities, as I said it is only where we are drawing the boundry, and is just semantics.
we are agreeing to a large extent here it is just the demarcation point that differs.
As above, again you are of course correct, but then you are used to larger installations and you will no doubt be familiar with the entire supply network on your large projects, here we were just talking about a simple CU change in a flat, the installer will only certify from the cut-out in that flat, he is not going start chasing through the finer points of the DNOs building supply infrastructure as this is neither necessary nor desired, it would be complete overkill for a simple part p notification
Agreed again, lol, I already said this, I would still certify it as that flats Ze though, because that is the external earth for that particular flats supply, agreed not to the building, this is because of the way the EIC and the definition is given to a domestic dwelling, again I did say further back that flats can be awkward, if we are carrying out work in that flat we would only certify from that flats own single phase cut-out, to go any further would be overkill again.
That is true, nothing to disagree with here, this is just a normal set up, I said this was how the usual set-up was usually implemented.
Here you would have to take that up with UKPN lol, they stated the objectives and what was required in their documentation, they called this a hybrid system not me, this was a PME system according to them and not just the usual switchgear link, if I can post up the relevent page I will.
I cannot really argue with them lol, it is way above my payscale
My comments in Blue
The TNC-S incommer/flat scenario by the way was purely hypothetical but based on a real system, I haven't seen Simons flat, he could have a TNS or TT incomer for all I know. ;)
I mainly brought this particular scenario up to illustrate a point that not everything is black and white, there are lot's of grey areas, this was partly due to earlier discussions in the thread, and partly to where the OP (UK Sparks) assessor pulled him up saying because that particular service head was supplied from a split-concentric cable that it could not be TNC-S/PME. just looking at the responses here then clearly that is not true, it is possible to have a cut-out with no CNE link and a SNE and yet still be TNC-S/PME. ;)
I myself had a strange one, here was just a normal domestic house, nothing unusual at all, anyway the supply was originally TNS with the usual lead sheath, this had been converted by the DNO to PME with the link fitted but they had also bonded the Lead sheath as well.
This actually made sense thinking about it, but at first glances it looked as though it had both earthing systems at the same time! it was only by opening the head that I could see what had been done, the tests referred to to earlier (PSSC/PEFC) were substantially the same.
The pretty pics in the OSG of various heads and systems are mostly right, but there are a lot of variations out there, assume nothing lol.
Don't forget, the Regs are not the be all and end all. They are guidance and need to be complied with as far as is reasonably practical. It is better to bond where you can, than not to bond at all. I wouldn't be concerned about the 500mm rule, it wont take fault current much longer to travel 20 feet than it does to travel 500mm. Cable has a hell of a lot of redundancy built in, so i can't see your 6mm having any issues unless your PFC is off the scale.
Cheers..............Howard
Reply to New Consumer Unit in the Electricians' Talk area at ElectriciansForums.net
Good morning guys Was looking for advice with regards to installing an outdoor consumer unit. Customer is looking for power to be installed from...
Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
hello all...whats the typical cost for a new consumer unit fitted and the old wired fuse box removed im in a semi detached house in...
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Hi, Hoping someone can clarify for me. I've recently moved into a rental property, the landlord had new electric radiators installed and a new...