U
Underpaid
As a guide in the 17th the max Ze readings for the following =
Tns = 0.8
Tncs = 0.35
TT = 200
I Recently got a Ze reading of 0.15 on a Tns system, as its higher than 0.8 in the 17th should i be worried?
If its ok, what Ze readings would you consider high for each of the systems? e.g time to call the DNO.
Also filling out a certificate with a higher Ze reading than recommended in bs7671, allowed?
Tns = 0.8
Tncs = 0.35
TT = 200
with maths like that, you'll never make a scouse wheel thief. you'd nick1 and say it was more than 4!
Give the OP a break, most prob a brain fart moment....
Good grief!
Where exactly on BS7671 did you get that lot from?
There is no guideline maximum for Ze on a TT system, and if there was it's hardly going to be 200ohms is it!
Oh and 80 is higher than 15!
am new to testing so am sure i will make mistake, thats why i joined this site to get help from experienced electricians not to be bullied
well all i can say is the onsite guide should write it as 0.80, thanks tho that makes alot more sense than the regs
Tns = 0.8
Tncs = 0.35
TT = 200
Stop making out that scousers are thick