Discuss Ze Values? HELP in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
As a guide in the 17th the max Ze readings for the following =
Tns = 0.8
Tncs = 0.35
TT = 200
I Recently got a Ze reading of 0.15 on a Tns system, as its higher than 0.8 in the 17th should i be worried?
If its ok, what Ze readings would you consider high for each of the systems? e.g time to call the DNO.
Also filling out a certificate with a higher Ze reading than recommended in bs7671, allowed?
Tns = 0.8
Tncs = 0.35
TT = 200
with maths like that, you'll never make a scouse wheel thief. you'd nick1 and say it was more than 4!
Give the OP a break, most prob a brain fart moment....
Good grief!
Where exactly on BS7671 did you get that lot from?
There is no guideline maximum for Ze on a TT system, and if there was it's hardly going to be 200ohms is it!
Oh and 80 is higher than 15!
Tns = 0.8
Tncs = 0.35
TT = 200
Stop making out that scousers are thick
Hi,dude, You will have to grow a sense of humour,as you have only had 20% of the 100% normally given,which is,after all,only one seventh....:conehead:
Reply to Ze Values? HELP in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Cable calcs using cable calc app Working out cable size for a workshop. 100m long, 100a supply, mccb 100a zs- 0.23 ohms, in a duct on its own...