yea 4mm is plenty, thats why i say its a bit of a run and not a hell of a run. I will be checking appendix F though.
yea 25A mcb makes total sense now, thanks
Well how are we supposed to know what a bit of a run means, to my mind that implies a longish run. And without the design current how are do you know what size is ok for VD?
Ok sorry dave, My basic question was just about what's an acceptable protective device associated with a 25A rotary isolator. As i'm used to 16A, 20A or 32A.
You can't really rate the protective device based on the rating of the isolator, if that isolator is in fact a switch aswell as an isolator you will find that it has different ratings for different types of load.
Surely that's not SY cable installed outdoors?
Yes... What's your point?
I appreciate SY is not the best cable to use, but it does the job.its only a small section that is visible, the rest is under the decking and that section will be decked over shortly so not too bothered about UV issues.
Reason for sy, it's got a slight bit more protection from accidental damage, ok not tonnes, but a bit more than flex.
Maybe flex would have been better, but gin that eventually goes dry etc.
SY cable has a clear PVC sheath and, in general, is not recommended for outdoor use.It is intended for indoor use where some mechanical protection is needed. Outdoor installation is, in general, not recommended. The clear sheath is PVC and may have little UV protection and degrade quickly. some manufacturers claim that their SY cable is suitable for outdoor use though.
When an air con installer asked for a 25A isolator are they expecting a 20A or 32A supply to it?
I have installed dozens if not more than dozens of air con supplies and it is usually a 32 amp Isolator fed by a 6mm2 supply, obviously the cable size will be determined by the length of run, pretty standard 32 amp and 6mm2.
why 6mm and not 4mm?
Jackflash,
davesparks,