yea 4mm is plenty, thats why i say its a bit of a run and not a hell of a run. I will be checking appendix F though.
yea 25A mcb makes total sense now, thanks
Ok sorry dave, My basic question was just about what's an acceptable protective device associated with a 25A rotary isolator. As i'm used to 16A, 20A or 32A.
Here's a 40A isolator i fitted today when I put a 32A circuit in for the hot tub.
View attachment 28828
Surely that's not SY cable installed outdoors?
Yes... What's your point?
I accept that. I've got another next week, I'll put some black flex on it.
I accept that. I've got another next week, I'll put some black flex on it.
flexishield or NYY-J cable could be used.
I have installed dozens if not more than dozens of air con supplies and it is usually a 32 amp Isolator fed by a 6mm2 supply, obviously the cable size will be determined by the length of run, pretty standard 32 amp and 6mm2.When an air con installer asked for a 25A isolator are they expecting a 20A or 32A supply to it?
I have installed dozens if not more than dozens of air con supplies and it is usually a 32 amp Isolator fed by a 6mm2 supply, obviously the cable size will be determined by the length of run, pretty standard 32 amp and 6mm2.
Client request, and why not 6mm2?why 6mm and not 4mm?
Client request, and why not 6mm2?