Discuss contactor rating in the UK Electrical Forum area at ElectriciansForums.net
S
Shaun12
When looking at contactors, does the coil voltage refer to auxiliary a1/a2 such as 24v supplied from a plc output and contact voltage rating refers to the feed/load being switched? If a contactor is rated to 690v/3-pole could it be used for 415v/3pole or 230v single pole?
A1 & A2 are the coil voltage to operate the contactor, the voltage switched is only relevant to the current being switched. So the voltage is not a issue, as the contactor rated for 690v will switch any voltage below its rating. The current rating will however decrease on lower voltage and if used for DC switching
Any voltage can operate a controlling coil for a contractor switching any voltage.
It should noted though that many old contactors may still have a 240/415v coil
You must make sure though that all supplies are from the same main source of supply even if a transformer is used, if not it should be indicated that there are 2 sources of supply.
Don't understand this bit Tazz, did you mean to say the power rating?
Thanks for the replies.
Would this be classed as a contactor?
What is the part sitting out from the main unit?
Thanks.
Oh what's the difference then? They both operate in the same way with the same idea a coil making contacts when energised. So when does a relay become a contactor?
Contactors have the ability to switch higher currents and are made to suit whilst relays normally switch much lower currents such as control circuits etc. You can purchase mini contactors which are the same form factor as the relay you have there.
What is it you are wanting to do with this?
These are seimens range of compact contactors and usually for the lower loads ...as for the difference between them well I never really thought about it, but often relays tend to be limited load handling ...
This isn't technical but if clicks, its a relay and if it clunks, its a contactor ;) (Excluding solid state device before I get a smart comment :p)
Thanks.
Generally speaking a contactor is used to switch a load and a relay is used within control circuits.
But there is no hard and fast definition to either.
Generally contactors have higher current ratings and switching duties, but you can also get relays capable of switching 100's of amps.
The tell-tale sign in your picture are the markings, these denote normally open and normally closed contacts which are usually found on relays of that type, contactors on the other hand are marked up differently L1, L2, L3 etc.
That doesn't necessarily make it a relay though, it could still be a contactor.
Some of the other writing on there is a bit more useful in getting reliable identification, specifically the part number. A quick google brings up a data sheet clearly tilted 'contactor'
clunk -click. thought jimmy saville was brown bread.
I'd say it's a contactor, that's what I ask for when I need one of these lol, relay and contactor are essentially the same thing, as has been said it is usually higher switching currents with a contactor, but whatever the manufacturer calls it.......
I didn't realise a contactor could be switched using Normally open Or normally closed contacts like a relay can be switched, I thought they were coil controlled?
Interesting thread, my thoughts are that a contactor is either open or closed and used to switch on/off and for switching high loads.
whereas a relay is for control switching with a common and n/o n/c. So a relay can be used as a contactor but not the other way round.
So if I'm right, the picture is of a contactor as it has no common, although it has independent n/o n/c contactors it cant switch from one to the other.
Relays can have single contacts or any combination of contacts though. Daz
Reply to contactor rating in the UK Electrical Forum area at ElectriciansForums.net
Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Hello People Our Enphase solar system needs to have the AC supply shut down via the fire alarm contactors local input output unit that has NO &...
Hello, I’m need some advice on how a contactor is wired please and where the neutral go. I’m told it is connected to eco 7 and controls 3 heaters...
Hi. Can anyone offer a bit of advice please. I've got a customer who wants needs an upgrade to their consumer units. It is a bungalow that has a 3...
7K
