gazdkw82
my sister has asked if i will install a shower for her when i have sufficient knowledge and experience.
iv been going through some figures as a little practice whilst im not very busy.
This is the CU set up
TNCS supply
------------CCU------------
downstairs sockets - 32A - 32A with diversity
downstairs sockets 32A - 12.8A with diversity
downstairs lights 6A - 3.96 A with diversity
upstairs lights 6 A - 3.96A with diversity
Cooker 32A - 16.6A with diversity
Heating 16A - 13A with diversity
total demand 82.32A
the supply fuse is 80A
before i even consider installing a shower in the future would the supply fuse have to be upgraded by DNO?
am i going about this the right way?
TNCS supply
total demand 82.32A
How have you arrived at these figures?
What you have to remember is that all of them loads are not going to be running at those figures at the same time. If you clamped it you would probably find its no where near those figures the majority/all of the time. IMO it would probably be under 6A most of the time.
6A? You mean 60A?
i haven't even added the shower to those figures. The shower she has is 35A!!
That would put total load at around 120A on a 80A main fuse.
Is that feasible?
6A? You mean 60A?
Is that feasible?
No, he means 6A, a domestic installation will have a surprisingly small average demand.
Most appliances are only on for short periods of time, and rarely pull their full rated current for much of that time.
I'm looking at the energy monitor for my house at the moment and the demand is a whopping 0.017kW! That is just the fridge, freezer and modem on.
If I turn the TV and associated crap on then it goes up to 0.050kW.
That's a far cry short of what the calculation would suggest!
The bottom line is that you need to take a look at what is actually used. On a bigger job you'd likely measure the actual demand using some form of data logger, but that's rarely fragrance for a domestic job!
Ok so I could go round and amp clamp the meter tails during an evening when most demand is being used??
6A? You mean 60A?
Is that feasible?
You need to remember, how long will the shower be on? not all day a few minuets at most. like wise any other heavy loads, kettle, etc. probably as small a load as has already been mentioned is correct
I understand and what your saying but there must be actually rule of thumb to achieve a real average figure that can actually be used if there was ever a problem
Didn't do a lot of Domestics gaz, but don't recall hearing of a rule of thumb, maybe one of the Domestic Installers guys could help.
I have an example that will mix things up :) We recently installed a fire alarm system in a 14 bedroom guesthouse. The guesthouse was fed from a standard 100A domestic supply. From memory there was 6 ring circuits, 4 lighting circuits, cooker circuit, 2x 3kw immersion circuits and a heating circuit oh and how could I forget 10(!) electric showers ranging from 8.5-10kW each!
The owner said he has never had an issue with the electrics or blown DNO fuses in the 10 years he has owned the property!
Sent from my SHIELD Tablet K1 using Tapatalk
That can't be true!???
gazdkw82,
Baker1988,