G
Gigsy
Can anyone help me understand Zs values.
In the On-Site-Guide page 60 Table 7.1 under the heading Maximum cable length, it states if
Zs < 0.35 ohms for a TN-C-S system
you can have a cable length of 107m
In BS7671 page 58 Table 41.3 it states the
Maximum Zs for a 32A CB to operate within 0.4s is 1.37 ohms.
It was my understand that Ze is 0.35 for a TN-C-S system, so why does it state Zs as being 0.35 ohms in the On-Site-Guide. Is this a mistake in the OSG, should it be Ze not Zs?
I was looking for the maximum Zs of a circuit in the ONG, but I can not find where it is, Does anyone know if the OSG has a reference to maximum Zs values, surly they have to be in there?
Hey Gigsy - check out appendix B of OSG, Table B6 has B type MCBs (original table has errors, there's a stick on page update in mine).
I think you're right about the use of Zs on p60, should be Ze (ie Ze <= 0.35 for TNCS)
Reactions: Davisonp
Thank you, that is the table I was looking for. So that was the table that came with my OSG. I have two copies of the OSG and I have lost the correction table from both :(
They do not make that table easy to find do they. Thank you!
In BS7671 Table 41.3, page 58 states:
The Zs for a 32A type B CB to trip in 0.4s is 1.37 ohms
The On-Site-Guide, Table B6, page 125 states:
The Zs for a 32A type B CB to trip in 0.4s is 1.1 ohms
Is this the table that is wrong?
Tables in on site guide for max lengths of circuits assume a maximum volt drop of either 3% for lighting or 5% for other circuits.
Example
20amp type b cb with 2.5/1.5 cpc
5% volt drop is 230 x 0.05 is 11.5 volts
11.5 x 1000= 11500
Ib x mv/a/m 20 amp x 18 mv/a/m for volt drop = 360
11500/ 360= 31.9
Table 7.1 page 64 gives max length as 31 meters
For 20amp cb type b
No its 1.37 x 0.8 for temp correction = 1.10 ohms
See appendix 14 in bs 7671
On site guide gives values with on site testing temperature adjustment
Example
11.5 x 1000= 11500
11500/ 360= 31.9
For 20amp cb type b
Good maths, but why are you telling me about the maximum lengths of cables in regard to voltage drop, when the question is concerning maximum Zs values?
Another way is 1.37 x 0.96 to adjust to 10 degrees = 1.31/ 1.2 to adjust to 70 degree cable operating temperature is 1.10 ohms
because table 7.1 which you mentioned deals with max lengths of circuits regarding volt drop
Thank you, it adds up. Wonder what temp. the values in BS7671 are based on then?
70 degrees max operating temperature of cables
Remember when a circuit is in use it will be operating at a certain temperature.
Bs 7671 assumes worst case scenario of max operating temperature of 70 degrees hence the maximum zs allowed
It is interesting you mentioned 0.96 as a correction factor.
page 58 of BS7671 Note 1, states they used a correction factor of Cmin 0.95 to account for the potential voltage drop of the supply.
Is it a temp correction value or do you think BS7671 has accounted for Cmin and the On-Site-Guide has not?
  • Informative
Reactions: Alshaw
Cmin is applied to 230 v and is 230 x 0.95 = 218.5volts
The 0.96 is to temp adjust to 10 degrees nothing to do with each other.
You know your stuff, your math is spot on!
You are correct in saying BS7671 gives values of max Zs permitted max operating temp is not exceeded (Note 2).
You are correct in saying that values in OSG are given based on ambient temperature.
I agree that Cmin and temperature correction values are different things.
Thank you for your help :)
Reactions: Rpa07 and Ian1981
So Cmin is applied to both tables then? The OSG also factors in a temperature correction factor, that is the reason the values are different?
A type b mcb will trip between 0.1-5 seconds at 5 x the rated current
So 32amp x 5 = 160 amp
So 230v x cmin 0.95= 218.5 volts
218.5/160= 1.37 ohms
1.37 at 70 degrees
1.37 x 0.8 = 1.10 ohms
Reactions: Gigsy
I still do not get it, so why does the OSG say 1.1 again?
Calculation in OSG
32 x 5 = 160A
230 x Cmin 0.95 = 218.5V
218.5 x Ctemp 0.96 = 209.2
209.2 / 160 = 1.3 ohms
Calculation in OSG
32 x 5 = 160A
It's 1.37 x 0.96
It's the zs your using temp correction with not the voltage
Reactions: Gigsy
It's 1.37 x 0.96
1.37 x 0.96 = 1.31
OSG says 1.1
I guess what you said to start with is the reason, they are using different conductor tempertures for their calculations, or something.
Thank you for your time, why they do not print the same information frustrates me, it makes learning very confusing.
It's 1.37 x 0.96
So say if I measured Zs at 1.3ohms and looked at the table in the OSG and it said it should not be greater than 1.1ohms, should I be concerned? Or just ignore the OSG and use the values in BS7671
It's 1.37 x 0.96
1.37 x 0.96 = 1.31
OSG says 1.1
1.37 x 0.96 = 1.31
1.31/1.2 = 1.096 or 1.1 ohms
The 1.2 is to adjust back to 70 degrees
I've made it too complicated just get your zs from bs 7971 and x it by 0.8 to get your max zs when testing at site temperature
Reactions: Gigsy
1.37 x 0.96 = 1.31
Thank you :)
You are good.
If the zs is too high when testing at site temperature then it will be safe to say it will be too high at cable operating temperature.
We can't test when cable is running at operating temp which is why we adjust our values for testing at site temperatures
the osg assumes a worst case of the cable operating at 70 degrees. except in some industrial situations, this is extremely rare. e.g. i once had a 16mm T/E running at 110A for 30 minutes. temp. did not exceed 40 degrees.
hnd in electrical engineering
i got that and i ain't that good. forgotten too much.
Make you wonder if these cables actually can run at more amps in the different reference methods given by bs 7671 or they just play it too safe?
Understanding Zs values
Gigsy,
Ian1981,