But the zero ohm reading shows that there is either a fault or something is still plugged in. Without unplugging everything how will you know which it is? The test result is meaningless.
Not entirely meaningless. Just not the value you would have hoped for. If you can get an acceptable IR value with appliances connected, you know it's going to be OK without them. Obviously, if the IR's too low then further investigation required.
 
Not entirely meaningless. Just not the value you would have hoped for. If you can get an acceptable IR value with appliances connected, you know it's going to be OK without them. Obviously, if the IR's too low then further investigation required.

But he hasn't got acceptable values.
 
It is odd he hasn't got zero both sides to earth but he also has a reading for L/N.
 
The burnt neutral looks to me to be on the lighting circuit..must have been loose.
I would agree that all would need to be unplugged for IR test and the imm htrs would need to be switched off if double pole switch or disconnected if only single pole kit eg some spurs maybe for washing machine?

Wonder what live to earth on ohm scale showed?
 