A
apprentice123
just a quick question about galvanised trunking in a commercial setting with regards to an assaignment ive been set by my college.
i have got a run of trunking running from a plant room in a car garage which will carry pvc singles for sockets lighting etc, alongside this i have to get 4 cat 5's and 3 fp200 cables for the fire alarm system. would it be acceptable to run all of the cables through the same trunking using galvanised filleting to segregate the voltage bands and segregate the fire cables? if it is how would i go about bringing the cables over one another when they need to cross over within the trunking?
you would be looking at 3 compartment trunking prob. 150x50 and you could use manufactured cross-over tees ect. or you could just drill holes in bottom or sides and use conduit to points
Jobs that I’m on in commercial settings almost 100% of the time the spec insists on fire alarm cables being kept away from other building cables using appropriate segregation, and I’m not 100% sure but does bs 5839 -1 not recommend this?
Just re-read question so could be in trunking or could be clipped direct to building fabric or on separate basket or tray its a bit open-ended
sorry there is drawing that go along with this that show that the trunking will be fixed directly to a block wall along the length of its run, all cables will leave the trunking in galv conduit out of the bottom of the trunking meaning that i would need to cross cables across each other at different points along the length of the trunking. meaning i would need a way of crossing said cables without mixing band 1 and band 2 cables.
If you can post a copy of the drawing and exact question you may get a more precise answer.
why not just have a seperate containment for the cat 5/singles/FP
you could then make brackets to hold trunking, any conduit drops you could make offsets to reach the wall and drop as normal
that way you avoid crossing cables at drops
You can notch the internal seperator to allow for a piece of 20mm plastic conduit, this allows the cat 5 to pass through the 230v compartment and vice versa, then you just bush onto the the trunking as normal.
If you went down the 3 comp.truking route you could drill drill say 20mm hole in the bottom of trunking then continue drilling in the same line through to the next compartment ect. sending conduits through to the respective compartments,but it would compromise trunking capacity.What about bending radius of cables?
Why would they need to cross each other?
The trunking will have a divider in it which separates the two voltage bands. Drill out the bottom of the trunking where you need the cables to exit and tube from there on to final position. Or am I missing something ?
would it not be bad practice to do so though? ive never seen data cables in the same containment as 230v
usually kept very very seperate
On all the jobs i work on the data has its own basket so not something i have had to think about personally.
528.1 (iii)?
528.1 (iii)?
dado trunking must have the sort of set up with dividers so must be allowable, just seems "wrong" to have data cable in the same trunking as 230v
usually on bigger jobs the data/fire protection is subbied out so never had to worry about it either really lol