Hi all,
I was hoping to sneak in a little job late this afternoon - changing a faulty bathroom pull chord for an outside switch plate. No problems with access. Straight forward enough.
House is almost certainly post 60's. CPC's present in lighting circuit.
Live Zs = open circuit.
R2 test with wander lead from MET to as many lighting JB's in the loft I could find = 60 k ohms.
So there is some sort of reading.
Loose connection?
Back tomorrow so any advice on where to start always appreciated.
It looks like the lights are wired in single line + cpc, looped in an out using every which method you can think of, and a neutral looping around each load.
Like I said - where to start.
There are other circuits available in the loft - I could bridge across from 1 JB to another with some 4.0mm if I have to (I suppose).
Does the home owner have the certificate for the installation of the CU? The schedule of test results could make interesting reading
I’ll ask. I was thinking that because I was getting 50k ohms rather that complete open circuit that the install designed to be earthed but something has gone wrong somewhere. I have already sorted out a couple of tapped up connections outside of enclosures - that sort of thing.
Reply to High R2 - Lighting Circuit in the UK Electrical Forum area at ElectriciansForums.net
Ok I’ll try this when I’m down
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...