N
Nigel
This would be a hell of lot more economical than making the system a TT and doing away with a stable earth in favour of an unstable earth.
hmm yes Essex i think this would be the best way to go, as long as all final circuits will meet the required disconnection time then we have no issues.
I think converting to a TT is money for old rope, would the 500ma downstream RCD just to for backup and to protect the tails?[/QUOTE]
No
It is to provide circuits that exceed the max permitted Zs fault protection.
A 500mA RCD has a max permitted Zs of 100 ohms so is good.