Naughty, naughty.He would usually make a derogatory comment about landlords
No offence intended Burnsy!
Naughty, naughty.He would usually make a derogatory comment about landlords
No offence intended Burnsy!
never said anything of the sort!My point is that you stated that not meeting maz permitted Zs values was grounds enough to go back to the DNO.
I am just pointing out that that is rubbish.
never said anything of the sort!
Your design would be a non starter.
We are talking about a hypothetical ze of 0.85 you have brought to a scenario not in relation with the OP ze problem.
Stop looking for confrontation, if you want that go join Twitter and spout aload of nonsense to complete strangers.
I normally wouldn't apply the temperature correction to the suppliers network for this reason.... temperature correction ... will it ever reach 70 degrees? In most cases probably not.
I agree. Ze being outside their own target and DNO not fixing means it's only going to get worse. The installation should not be left in this state.I would be constantly checking the Ze on the existing system to see if it falters and check any neighbouring premises for comparison.
.That Ze maybe perfectly stable and as I said before those max values are not carved in stone.I agree. Ze being outside their own target and DNO not fixing means it's only going to get worse. The installation should not be left in this state.
On the plus, SSE recently improved my home TNS Ze from 0.6 to 0.5 - I noticed a new (bigger) transformer has been installed locally and no doubt they've cleaned everything up. Proper planned preventative maintenance.
So when you say building, what kind of building it? Domestic or ...?
I think what I am trying to say and has been alluded to, if you have a Ze of 1.25 ohms and there is say an RFC which will require a Zs of 1.37 that will give you a wapping 0.12 ohms for compliance with disconnection times via an MCB for OCP on your Zs.
No but the regulations always work to the worst case scenario so I always stick to the maximum zs stated in appendix 3 but when testing at site temperature, it is taken into account.I normally wouldn't apply the temperature correction to the suppliers network for this reason.
The building is a small hut in the middle of a park which has a few ring final circuits for heaters and lighting etc, the Ze is stable, give or take 0.05 over 3 months.That Ze maybe perfectly stable and as I said before those max values are not carved in stone.