I used it on my SDS max and it saves loads of effort.I bought one of them ages ago, never used it in anger yet. Interestingly, mine hasn't got a hole at the end![]()
The DNO are obliged to maintain the earth they have there REG 25 ESQCR. Tell them you will take it up with HSE if they will not. They can put a steel band around the intake cable and braided earth from that. There is no excuse for them not to comply. Kick some arse!
Correct. Here we go again, the fog is descending. If it's a TNS supply, then get the DNO out to sort it out, end of story. Next?Surely they should come out and sort their earth out.
1.25ohm external earth fault loop impedance on TN-S supply to building is functioning then is it?The earth is in place and functioning.
1.25ohm external earth fault loop impedance on TN-S supply to building is functioning then is it?
Max value for TNS is 0.85 off top off my head. That's what DNO's have to work to. Either it is, or it isn't.Yes it is. May not be optimal but most likely all OCPDs will not exceed their maximum permitted ao what is the issue?
Incorrect. It's well out of spec for a TNS system. Simple. Argue as much as you like, it's out of spec.Yes it is. May not be optimal but most likely all OCPDs will not exceed their maximum permitted ao what is the issue?
So what is your Zs on say the RFC?The earth is in place and functioning.
With the 80% rule of thumb? 1.06 so would not meet required disconnection time as already alluded to.1.37 ohms max zs for a32 amp type B so unless