What is this SDS adapter as i normally use a club hammer?
SDS-Earth-Rod-Driver-Socket.jpg
 
I screw an earth rod driving bolt 5/8 into a rods coupler, then use an sds nut driver with the appropriate size socket, drill on hammer and rotostop. Don't expect to be able to use the nut driver and socket for anything else though
 
The DNO are obliged to maintain the earth they have there REG 25 ESQCR. Tell them you will take it up with HSE if they will not. They can put a steel band around the intake cable and braided earth from that. There is no excuse for them not to comply. Kick some arse!
 
The DNO are obliged to maintain the earth they have there REG 25 ESQCR. Tell them you will take it up with HSE if they will not. They can put a steel band around the intake cable and braided earth from that. There is no excuse for them not to comply. Kick some arse!

The earth is in place and functioning.
 
Yes it is. May not be optimal but most likely all OCPDs will not exceed their maximum permitted ao what is the issue?
Max value for TNS is 0.85 off top off my head. That's what DNO's have to work to. Either it is, or it isn't.
Yes it is. May not be optimal but most likely all OCPDs will not exceed their maximum permitted ao what is the issue?
Incorrect. It's well out of spec for a TNS system. Simple. Argue as much as you like, it's out of spec.
 
1.37 ohms max zs for a32 amp type B so unless your R1+R2 is ridiculously low then your max zs for this circuit will be exceeded.
I do not know what overcurrent protection is involved in this instance nore no of any rcd protection but no one in their right mind should except that ze measurement on that particular earthing arrangement.
 
I who hazard a guess that the DNO fuse would also not disconnect in the required time 5seconds if there was an live to earth fault on the tails.
Same statement could be said about a TT arrangement, however it’s not a TT arrangement at present.
 