W
westos-electric
Hi
I need help working this cal. Please can you confirm the answer and how it's worked out?
Question
A conductor 500mm long is placed in at right angles to a magnetic field with a magentic flux density of 0.25 tesla. What is the current required in the conductor to create a force of 15N on the conductor.
Hope you can help
Wayne
Hi
Question
Hope you can help
Wayne
F = BIL
rearrange to I= F ÷ (B x L)
Edit : remember length must be in metres
No just trying to get some extra help, I've the text books and done the revision but still finding it hard.
You arn't doing my homework, this was my last call.
if its any consolation I seem to remember there was a similar question at the end of one of the chapters in my b & b course notes for the 202, but when i looked back over the chapter they had not actually covered that particular equation. however i eventually found it in Scaddan's electrical installation work.
write a list of all the formulas you have learned
carry it around with you
read it often
think of ways to help you remember them:
for example the Force formula would be the police force is the old bil so F=BIL
then learn transposition with that you can easily rearrange most formulas to find what you need.
Hi
Is anyone able to check my answer on this?
A 12v battery is connected across a set of resistors in series, values being 60, 30, 100, 45ohm the current in the circuit is?
60+30+100+45 = 235 12/235 = 0.053x1000 = 52mA
is this correct?
also one more thing Power factor is at unity when?
Cheers
Wayne
Hi
is this correct?
Cheers
Wayne
51mA
PF is at unity (1) when voltage and current are exactly in phase. This occurs in purely resistive circuits or when an inductance exactly counterbalances a capacitance in the same circuit.:)
edit : 12/235 = 0.05106
Hi
wondered if anyone could point me in the right direction re-
A heater supplied from a 230volt/50hz star connected system with a load current of 19.5A. Calculate the power used
a 3kw is supplied for a 230 volt/50hz system with a 0.7 cos calculate the supply current.
Hi
A heater supplied from a 230volt/50hz star connected system with a load current of 19.5A. Calculate the power used Single phase? just use P = I x V
Single phase
power = I x V x PF
I = power / (V x PF)
Question
A capacitor of capacitive reactance 5ohm an inductor of 8ohm inductive reactance and resistor of 4ohm are connected in series to a 230v 50hz supply. The total impedance of the circuit will be?
5ohm
This is a question on a sample paper but i can't seem to work out how to do the working out
Can you help?
Cheers
Wayne
Question
5ohm
Can you help?
Cheers
Wayne
the capacitor and the inductance are producing opposite effects to each so you just want the difference between them.
look at your impedance triangle and you have sides of 4Ω (resistance) and 3Ω (reactance 8-5) you just need to find the hypotenuse :)
Hi
I've tried working this question out but getting something wrong.
Question
A 30kW 3 phase delta connected motor has a power factor of 0.86 lagging. calculate the line current
I thought it would be
30,000 / (400x0.86) but doesn't match the correct answer which is 50.35A
Could you confirm where i'm going wrong?
Wayne
westos-electric,
dichroic,