Discuss Help on an exam question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
W
westos-electric
Hi
I need help working this cal. Please can you confirm the answer and how it's worked out?
Question
A conductor 500mm long is placed in at right angles to a magnetic field with a magentic flux density of 0.25 tesla. What is the current required in the conductor to create a force of 15N on the conductor.
Hope you can help
Wayne
Hi
Question
Hope you can help
Wayne
F = BIL
rearrange to I= F ÷ (B x L)
Edit : remember length must be in metres
No just trying to get some extra help, I've the text books and done the revision but still finding it hard.
You arn't doing my homework, this was my last call.
if its any consolation I seem to remember there was a similar question at the end of one of the chapters in my b & b course notes for the 202, but when i looked back over the chapter they had not actually covered that particular equation. however i eventually found it in Scaddan's electrical installation work.
write a list of all the formulas you have learned
carry it around with you
read it often
think of ways to help you remember them:
for example the Force formula would be the police force is the old bil so F=BIL
then learn transposition with that you can easily rearrange most formulas to find what you need.
Hi
Is anyone able to check my answer on this?
A 12v battery is connected across a set of resistors in series, values being 60, 30, 100, 45ohm the current in the circuit is?
60+30+100+45 = 235 12/235 = 0.053x1000 = 52mA
is this correct?
also one more thing Power factor is at unity when?
Cheers
Wayne
Hi
is this correct?
Cheers
Wayne
51mA
PF is at unity (1) when voltage and current are exactly in phase. This occurs in purely resistive circuits or when an inductance exactly counterbalances a capacitance in the same circuit.:)
edit : 12/235 = 0.05106
Hi
wondered if anyone could point me in the right direction re-
A heater supplied from a 230volt/50hz star connected system with a load current of 19.5A. Calculate the power used
a 3kw is supplied for a 230 volt/50hz system with a 0.7 cos calculate the supply current.
Hi
A heater supplied from a 230volt/50hz star connected system with a load current of 19.5A. Calculate the power used Single phase? just use P = I x V
Single phase
power = I x V x PF
I = power / (V x PF)
Question
A capacitor of capacitive reactance 5ohm an inductor of 8ohm inductive reactance and resistor of 4ohm are connected in series to a 230v 50hz supply. The total impedance of the circuit will be?
5ohm
This is a question on a sample paper but i can't seem to work out how to do the working out
Can you help?
Cheers
Wayne
Question
5ohm
Can you help?
Cheers
Wayne
the capacitor and the inductance are producing opposite effects to each so you just want the difference between them.
look at your impedance triangle and you have sides of 4Ω (resistance) and 3Ω (reactance 8-5) you just need to find the hypotenuse :)
Hi
I've tried working this question out but getting something wrong.
Question
A 30kW 3 phase delta connected motor has a power factor of 0.86 lagging. calculate the line current
I thought it would be
30,000 / (400x0.86) but doesn't match the correct answer which is 50.35A
Could you confirm where i'm going wrong?
Wayne
Hi ive still had issues with this question
A small heating circuit draws 1.5kw of power and has an internal resistance of 0.5ohms what is the current drawn?
I've been reading about transformers and need help on this question
A transformer has an output of 12kva and a power factor of 0.9. the total losses in the transformer are 600w. What is the efficiency of the transformer
now i know / think the formula is output/ output power + losses
I'm not sure how this works out, can anyone help
cheers
cheers
The formula you require is:
input power = output power + losses
However you need to use:
Efficiency = output power / (output power + losses)
so: Output power = KVA x Power factor
12kva x 0.9 = 10.8kw
Efficiency = 10800 / (10800+600) = 0.947
0.947 x 100 = 94.7% efficient.
Regards
Dichroic
Reply to Help on an exam question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
Hello, I need to conduct interviews with experts in the relevant field for my university project. The topic and product that I’m developing a...
Hi to everyone, this is my first post so if is been already asked/answered please guide me to the relevant discussion/thread. I don't know...
signed up to 247 training uk with payments associated with Carnegie Consumer Finance paying £180 per month. I did 9/39 models to do the pre...
4K
Please be as honest as you can all, I'm looking for real honest views before I waste thousands of pounds and my few remaining years of working...
Electrical Courses