It does not apply to a PME supply, but it could be used for a TNS suppy.I agree about the adibiatic not applying to bonding that's how I read it
It does not apply to a PME supply, but it could be used for a TNS suppy.I agree about the adibiatic not applying to bonding that's how I read it
but it could be used for a TNS suppy.
I think it can Dave, the reg's state 'not less than half the csa required for the earthing conductor'.Not really, the adiabatic is can be used to select the size of earthing conductor, then the bonding conductor is worked out based on the earthing conductor. The size of the bonding conductor isn’t a direct result of the adiabatic calculation. And if the earthing conductor size has been selected according to the table then the adiabatic has nothing to do with the bonding conductor size.
For example if the adiabatic shows that a 19.7mm earthing conductor is needed you would use 25mm, then the bonding would be 16mm (next size up from half of earthing conductor) if the adiabatic result was used for bonding it would be 10mm.
The adiabatic equation is not relevant to main protective bonding conductors, or any bonding conductors for that matter.No you are not obliged to do this unless you do the adiabatic equation and the 6 MM is not suitable.
If it's under 6mm then you are obliged to increase to 10mm for bonding and 16 mm for main earthing.
No need to wait, there has never been a requirement to bond plastic incomers.If you wait a couple of weeks and its got plastic incomer won't need bonding big tin hat on-off the cuff remark.
If you wait a couple of weeks and its got plastic incomer won't need bonding big tin hat on-off the cuff remark.