Ignoring the bonfire and what looks like a reversed supply, what size wiring is the supply cable?
what's that small box spliced in with the spade terminals?
if you have teenage daughters, you need to remove that. nothing gets them out better than a freezing cold shower.Inlet valve stop the shower from running if there no eleci
What watt rating is the shower?Just got back.
Loose connection
Wrong polarity at the shower. Correct polarity from C/U to pull switch.
Reterminated conductors, sorted polarity. Rcd tested fine and Zs was good. All good.
I did wonder that I could not prove what conditions the 6mm t+e was installed in the loft and around the house. If worst case scenario the cable is underated.
Without ripping the place apart I'm not sure how you can prove installtion method
If installation method can't be determined I apply worse case senario
Isn't 6mm t+e wise case around 34a? Or even further 29a?
I would say it was on the limit.