Friend says to me, "can you have a look at my shower. It smelt of burning, I turned it off and took the cover off. This is what's happened"

Oh ffs......

:mad:

received_296610074486643.jpeg
 
  • Winner
Reactions: ChipFanDave
Ignoring the bonfire and what looks like a reversed supply, what size wiring is the supply cable?
 
Ignoring the bonfire and what looks like a reversed supply, what size wiring is the supply cable?

I don't know, I'm going to have a look tomorrow.

I'm going to take a some 6mm and 10mm and take it as it comes
 
Looks like it could have been a poor connection
 
what's that small box spliced in with the spade terminals?
 
Inlet valve stop the shower from running if there no eleci
if you have teenage daughters, you need to remove that. nothing gets them out better than a freezing cold shower.
 
  • Like
Reactions: gazdkw82
"looks" likes a 6mm but could be wrong. Def. Wrong polarity. Most likely loose connection.
 
Just got back.

Loose connection

Wrong polarity at the shower. Correct polarity from C/U to pull switch.

Reterminated conductors, sorted polarity. Rcd tested fine and Zs was good. All good.

I did wonder that I could not prove what conditions the 6mm t+e was installed in the loft and around the house. If worst case scenario the cable is underated.

Without ripping the place apart I'm not sure how you can prove installtion method
 
Just got back.

Loose connection

Wrong polarity at the shower. Correct polarity from C/U to pull switch.

Reterminated conductors, sorted polarity. Rcd tested fine and Zs was good. All good.

I did wonder that I could not prove what conditions the 6mm t+e was installed in the loft and around the house. If worst case scenario the cable is underated.

Without ripping the place apart I'm not sure how you can prove installtion method
What watt rating is the shower?
 
If installation method can't be determined I apply worse case senario
 
Isn't 6mm t+e wise case around 34a? Or even further 29a?
I would say it was on the limit.

Agreed. I will speak with her tomorrow about upgrading it
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

gazdkw82

Arms
~
Joined
Location
leicester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Friends shower burnt out - fail
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
gazdkw82,
Last reply from
gazdkw82,
Replies
13
Views
215

Advert