Toneyz
Sorry I don't know how to post up a youtube link but have a look at the John Ward one part 2 on AFDD's worth a watch.
Thanks Anthony for the very informative post....probably need Michael more on the case![]()
Not really informative mate. The test was a farce.. Read post #15
It is quite alarming how these false videos are just taken as gospel by people as if millions of pounds of research would be wrong but an anorake in a shed with crap equipment is correct.
If, the maximum fault energy to cause a fire is required to be limited by an RCD to 0.3^2 x t, then why is it allowed to be 2.5^2 x t for an AFDD?
I know, I have access to the standard.Just to put it into context, if it was a 32A AFDD then it would be about 5A![]()
You are correct, in that RCD's do not protect against series faults, such as broken conductors, we have MCB's to protect against L-N faults.J.W. has just posted the third video with an electric heater and it still did not trip. RCD's are ok for faults to earth not sure regarding L-N and broken conductors. Look forward to the replies.
A 300mA RCD is not going to trip in the event of a fire, until the cables have melted enough, to allow earth leakage to occur.Don't forget, I mentioned nothing about additional protection by RCD, i.e. a 30mA device, I was referring to 0.3A devices, 300mA, for prevention of fire, as per BS7671 clause 422.3.9.