Firetrekker - what part of the UK is the job? Some EF folk might be close by and willing to help if you are a little stumped.
It is also worth sitting down quietly - with a pint, pen and some paper - and thinking through what it might be and how you could methodically discover or discount circuits/appliances. It will not be the last time you have to so good practice. Some good prompts already on test equipment you might borrow or buy and 'ways ahead'. So do some thinking before you next visit and sketch out a plan of attack. You might want to buy some RCBOs say 6A, 20A and 32A to leave some final circuits protected by them rather than the RCDs - in case the fault happens to be intermittent and not easily stimulated - then at your next visit you will have some new information from how they and the RCDs react.
So do some thinking before you next visit and sketch out a plan of attack. You might want to buy some RCBOs say 6A, 20A and 32A to leave some final circuits protected by them rather than the RCDs - in case the fault happens to be intermittent and not easily stimulated - then at your next visit you will have some new information from how they and the RCDs react.:)
Doesn't that rather depend on the CU make - it may not be able to be configured in such a manner
Eliminating appliances for accumulation is no good really..
You remove 1 non faulty appliance and hey presto all is ok. Replacement gets bought, plugged in and RCD trips again.
No , I’m going to ramp test the rcd against each circuit building up to full load, then see what the earth leakage is. I’m then going to see if I can re balance the splits and if not retro fit RcboS, I suggested these to start with but as usual they didn’t want the cost.
rally?
Hi all, to answer a few questions, there are two original circuits which is where I’m getting the low IR, I have ramp tested the reds but the house wasn’t full of stuff as there weren’t living there, so I will now again one circuit st a time, increasing until I get the full split powered up and then see what the earth leakage is. Then either rebalance board or go with rcbos. Thanks for all you help .
suggestion. with all loads connected, ramp test the RCD that's tripping, note the reading. then ramp test again with loads isolated. the difference in readings will be roughly equal to leakage. then try to track it down by adding loads 1 at a time.
Thanks ferg.
Where’s this Englandshire, sounds like a land of milk and honey :)
Firetrekker,
richy3333,